Safe Exhaust Recirculation of Manned Spray Booths
How to keep the cost of pollution control from hurting you…
Spray booths that use robots or automatically reciprocating paint application equipment are unoccupied during the paint process. For many of these unmanned spray operations, the time has passed for simple open-faced spray booths with all of the airflow exhausting out of the back filter bank plenum. During the last 15 years, spray booth exhaust has been recirculated in unmanned spray booths in more and more paint finishing systems. Now, unmanned spray booths are commonly equipped with recirculation fans, automatically advancing roll-up filters and ultra-fine return air filters. Recirculation has been done primarily to reduce the capital equipment and operating costs when air pollution control equipment for Volatile Organic Compounds (VOC) is required.
Case studies have shown examples of cost effective air pollution controls on recirculated spray booths where the Regenerative Thermal Oxidizer (RTO) or other control device is one-fourth the size and cost required without recirculation. When the savings from reducing heated air make-up costs are factored in, recirculation of spray booth exhaust can actually pay for the operating or running cost of air pollution control.
Similar savings can be obtained by recirculating spray booth exhaust in manned spray booths such as manual touch-up booths and large-part spray booths. However, return of air with VOC’s to an occupied space invokes important safety questions. Paint line supervisors may ask if painters will have to wear respirators or even fresh air masks. Plant management may wonder if this meets OSHA and fire safety codes. Here are some suggestions for the practical design and safe operation of manned spray booths with recirculated exhaust.
Fire Safety of spray booths with exhaust recirculation has been addressed by the National Fire Protection Association (NFPA) in its national consensus code entitled NFPA 33 – 2000 “Spray Application Using Flammable or Combustible Materials,” NFPA 33 Section 5.5.1 limits recirculation to when the actual VOC concentration in the return air is kept to less than 25% of the Lower Explosive Limit (LEL), and an LEL probe is interlocked to the spray operation. LEL’s typically run in the 5-10% range for recirculated spray booths.
Use of exhaust recirculation does not change the need for fire detection or fire suppression systems. But if some type of fire detection or fire suppression system is required, then these systems must be properly designed for the recirculating spray booth. For example, additional fire sprinkler heads in the return air plenum may be needed to effectively protect a recirculating booth.
Painter Health and Safety requirements are spelled out in OSHA’s respiratory protection standard (29 CFR 1910.134). This standard requires the use of approved respirators or other Personal Protective Equipment (PPE) when workers are exposed to actual paint solvent or VOC concentrations that exceed the OSHA Permissible Exposure Limit (PEL). PEL’s for commonly used paint solvents range from 50 ppm for toluene to 500 ppm for acetone. Since paint formulations contain a mixture of solvents, a Hazard Ratio must be calculated for each solvent by dividing the actual concentration of the specific solvent by its respective PEL. If any solvent Hazard Ratio is greater than 1.0, then a respiratory protection plan with PPE is required.
TABLE 1: Cost Effective Pollution Control Equipment | ||
Standard Design
Recirculated Booth Design
Automatic Booths (4) |
60,000 cfm
16,000 cfm
Manual Booths (4) |
48,000 cfm
0
Flash-off Areas |
0
3,000 cfm
Cure Oven |
4,000 cfm
4,000 cfm
Total Exhaust Flow |
112,000 cfm
23,000 cfm
Annualized Operating Cost |
$176,000/yr.
$21,600/yr.
Annualized Heated Air Make-up Cost Savings with Reduced Airflow |
($37,000/yr.)
Based on $0.06/KW, $4.00 per MM Btu, 100 lb/hr. VOC, Heated air make-up required 60% of the year. |
Keep in mind that some catalyzed paints have components with a very low PEL (0.02 ppm for methyl isocyanate). These may require use of PPE such as supplied breathing air for spray operations even if recirculation is not used. Also, it is very possible that adding recirculation to an existing spray booth may increase the actual exposure level by concentrating the solvents to a level above the permissible PEL. In this case, PPE must be used.
TABLE 2: Effect of Spray Booth Exhaust Recirculation | |||
No Recirculation
Partial Recirculation
Full Recirculation
Spray Booth Exhaust Rate (cfm) |
10,000
3,333
2,000
Paint Use (gal./hr.) |
5
5
5
Solvent Exposure (ppm) |
30
90
150
Solvent PEL (ppm) |
100
100
100
Hazard Ratio |
0.3
0.9
1.5
PPE Required |
No
No
Yes
Once the need to use PPE has been established, the next step is to select the proper type of PPE. PPE is rated by protection factors and each PPE manufacturer has approved products at various protection factor ratings. Generally, a half-mask respirator with particulate and organic cartridges has a protection factor of 10X. Full-face respirators with eye protection have protection factors to 50X, and supplied breathing air systems have protection factors to 1000X. At a minimum, the protection factor required for the PPE to be used must exceed the highest Hazard Ratio.
In situations where the PPE protection factor is many times higher than the highest Hazard Ratio, painter exposure to solvent in the recirculated booth may be lower than it would be without PPE and recirculation. Also, some painters prefer the use of more comfortable, battery-operated self-purging face masks (protection factor of 25X) over half mask respirators when the lower protection factor is still adequate for health and safety.
A health and safety professional should be consulted with when setting up any respiratory protection plan. This could be a large company’s corporate or plant level industrial hygienist. Smaller companies can use a representative from an established supplier of PPE as a resource. These professionals can help write the respiratory protection plan, provide training and medical referrals if needed, document fit testing and implement safeguards to assure PPE is always in good working condition.
Questions such as what is the permissible PEL, what is the actual exposure, and what is the best PPE may seem complicated. The important point is that there are scientific methods and OSHA procedures available to answer all of these questions. When required, PPE can be combined with properly designed fire safety features such as LEL interlocks to provide a safe manned spray booth with recirculating exhaust. As VOC pollution control becomes more widespread and applicable to smaller VOC emission sources, one is likely to see more recirculated manned spray booths.
Read MoreNASF/AESF Foundation Research Project #121: Development of a Sustainability Metrics System and a Technical Solution Method for Sustainable Metal Finishing - 15th Quarterly Report